I have two small grain bins that I can't seem to get power to. They ran for 5 years but something must of happened. I have a under ground 0 cable from the house to a barn then to another barn then out to the bin. I can't seem to get my head around whats wrong. I can get a voltage reading at 120 but not enough power to run any thing. so I thought maybe there is a break in the undergound cable. so I checked to see if the power meter was turning faster because of leakage to ground. but no change with the breaker on or off. If there was a break woundn't there have to be leakage and loss of power. I pulled the breaker and checked it with a VOM and it seems it Ok. I took a 12 volt battery and hooked it up to the two power cables back to the barn and I have 12.7 volts after a run of 100 ft. So that tells me the wires must be OK. What Am I missing?? There has to be something simple I'm missing???????? Any ideas will be helpful. Thanks
Solved! Go to Solution.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Re: electrical trouble shooting
sounds like you have lost one leg of your 220 in one of those barns. make sure all connections are tight
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Re: electrical trouble shooting
My motors are only 120, the 2 bins are just 1000 bu bins and the fans are just 3/4 horse fans. Although the voltage on the VOM reads 120 there is not enough power to run a shop vac I was try to use to clean out the bin but I can hear a low hum from the shop vac. One leg I lost last year to one of the bins but didn't need that bin so it wasn't important at the time now I lost the other one. I'd like to get them both back up but just can't seem to understand. Everything I check seems to say it should be working. Is it possible to have a breaker go bad but it still looks like its OK with a VOM? Can a wire break and still show 120 volts but not be able to move some amps? There is something I'm missing but I just can't get it.
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Re: electrical trouble shooting
You most likely have a loose connection somewhere. It will allow enough amperage through to read 120 volts on your meter but will not give you enough amperage to run any motors. Or the connection could be corroded,this would increase the resistance through the wiring.
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Re: electrical trouble shooting
I got a new breaker today but no change. Any resistance problms should show up as heat I would think. Wouldn't a cable break have some leakage to ground making my meter spin faster? when I hook up a 12 volt battery to the power cables I get the 12.6 volts at the other end of the cables. wouldn't that mean the cables are fine? everything seems to be tight. something here I'm not seeing. I'll hped to find the problem to keep me from digging up the cable.
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Re: electrical trouble shooting
Well I pulled out the line and half way between the two barns I found one leg and the ground totally corroded and gone for about 4 inches. All at the same spot. Insulation almost looked like it was cut all the way around but it wasn't clear what could of done the damage. It is not in a spot I drive on or park any thing. So I will never know. I think it must of been the frost heaves and a small crack let some water in. I live in a frosty place. Still found some Ice when I dug about 6 inchs deep. I just can't believe I got any readings when I was checking as bad as the break looked. the ground didn't look burnt or even dry where the break was. This stuff is just a lot harder to trouble shoot than I thought it should be or should be. Thanks for everyone's help in trying to think this out. Live and learn.
Bill